From the BP provisional 57 of the 70 trays within the column were flooded in the moment of the first explosion.
The splitter column have been out of service during one month and steamed out to remove hydrocarbons from February 26 to 28. The steam is usually prone to tray valves because after steaming the valves stuck with scale and after start up the vapor pressure of the ascendant gases is not enough to unplug the valves and the column get flooded. The flooding of the column was responsible for the high peak pressure of 63 psig when the maximum relief pressure was 42. In my opinion the high pressure in the splitter was responsible for the hydrocarbons release followed by explosions in downward equipment.
When tray columns are shut down for long time, just after start up is important to mechanically knock the valves or flush the column with water to dissolve the scale around them. The steam degasification should be done only just after start up.
Luis Marques
The splitter column have been out of service during one month and steamed out to remove hydrocarbons from February 26 to 28. The steam is usually prone to tray valves because after steaming the valves stuck with scale and after start up the vapor pressure of the ascendant gases is not enough to unplug the valves and the column get flooded. The flooding of the column was responsible for the high peak pressure of 63 psig when the maximum relief pressure was 42. In my opinion the high pressure in the splitter was responsible for the hydrocarbons release followed by explosions in downward equipment.
When tray columns are shut down for long time, just after start up is important to mechanically knock the valves or flush the column with water to dissolve the scale around them. The steam degasification should be done only just after start up.
Luis Marques