Pumprin
Mechanical
- Aug 13, 2014
- 10
Hi eng-tips, I have a project to install a booster pump into our existing cooling tower water system, and I would like your assistance on understanding the theory behind adding in a pump in series to one of the branches. I have attached a sample drawing.
The following will include reference to the sketch I attached.
The purpose of the booster pump is to incrase the pressure in Branch A so that the water pressure is higher than the process pressure. With the water pressure higher than the process pressure, any leaks would go from the water to the process instead of the other way around.
From the drawing, the system flow rate is much larger than branch A's flow rate, and the head produced by the P1 will by much larger than the head that P2 is capable of producing.
From reading from the Pump Handbook, I understand what the flow rate and system head of Branch A will be when P1 is running alone (Qa,Ta). However, I don't understand how Pump 2 would operate when added into Branch A. From the sketch, I just added P2 in series with P1, and it seems like since the total system curve doesn't intersect with P2's low flow region, P2 would do nothing.
I've attempted to play around with Pipe-Flo, but Pipe-flo seems to be unapplicable when sizing pumps in branch-line pumping.
Any reference material/advice would be appreciated. Thanks!
The following will include reference to the sketch I attached.
The purpose of the booster pump is to incrase the pressure in Branch A so that the water pressure is higher than the process pressure. With the water pressure higher than the process pressure, any leaks would go from the water to the process instead of the other way around.
From the drawing, the system flow rate is much larger than branch A's flow rate, and the head produced by the P1 will by much larger than the head that P2 is capable of producing.
From reading from the Pump Handbook, I understand what the flow rate and system head of Branch A will be when P1 is running alone (Qa,Ta). However, I don't understand how Pump 2 would operate when added into Branch A. From the sketch, I just added P2 in series with P1, and it seems like since the total system curve doesn't intersect with P2's low flow region, P2 would do nothing.
I've attempted to play around with Pipe-Flo, but Pipe-flo seems to be unapplicable when sizing pumps in branch-line pumping.
Any reference material/advice would be appreciated. Thanks!