Dear Colleagues
I have been having a problem with a breaker consistently tripping whenever I retransfer from Generator to Utility.It is a closed transition switch.
The problem is this, when ever you retransfer from generator to utility, the 200 amp 3-phase breaker will keep tripping. There is no motor loads connected to this breaker at all. It however has connected downstream around
10-15 ,415 V 15 KVA Transformers. All of which are single phase 110v secondary, powering lights, calculators. etc.NO motors at all.Could it be inrush from the Txs when I retransfer??
The problem i thought could have been motor related with inrush currents, when switching, but no motors are present. The in-phase monitor is also on, and swicthes around 8-10 degrees, but the breaker still trips. It does not trip when transferring from utility to genset however(remember the switch is between a dead source and a live one, when this occurs).
Please advise on what the problem could be and possible solutions. i have checked and the neutral and ground is bonded. The generator and utility both share the common. neutral and ground, so a switched neutral ATS
would not be necessary.
Could there be inrush of the Transformers, be a problem or not really?
> Can the problem be solved depending on the on the cause, by:
>
> An overlapping neutral switch and y?
> OR
> A delayed transition switch and y?
> OR
> any Type of surge protection on that breaker?
> OR
> Disconnection of that particular breaker prior to retransfer, via a load disconnect feature on the panel.
Any of your views will help. I have put a PQA on th esaid breker and it registered nothing prir to tripping.The breaker is a magnetis trip.Can the fast switch cause an instantaneous spike in the magnetis flux to trip the breaker?The breaker already ha sthe trip setting to max.
Thanking you all in advance
AMESOLUTIONS
I have been having a problem with a breaker consistently tripping whenever I retransfer from Generator to Utility.It is a closed transition switch.
The problem is this, when ever you retransfer from generator to utility, the 200 amp 3-phase breaker will keep tripping. There is no motor loads connected to this breaker at all. It however has connected downstream around
10-15 ,415 V 15 KVA Transformers. All of which are single phase 110v secondary, powering lights, calculators. etc.NO motors at all.Could it be inrush from the Txs when I retransfer??
The problem i thought could have been motor related with inrush currents, when switching, but no motors are present. The in-phase monitor is also on, and swicthes around 8-10 degrees, but the breaker still trips. It does not trip when transferring from utility to genset however(remember the switch is between a dead source and a live one, when this occurs).
Please advise on what the problem could be and possible solutions. i have checked and the neutral and ground is bonded. The generator and utility both share the common. neutral and ground, so a switched neutral ATS
would not be necessary.
Could there be inrush of the Transformers, be a problem or not really?
> Can the problem be solved depending on the on the cause, by:
>
> An overlapping neutral switch and y?
> OR
> A delayed transition switch and y?
> OR
> any Type of surge protection on that breaker?
> OR
> Disconnection of that particular breaker prior to retransfer, via a load disconnect feature on the panel.
Any of your views will help. I have put a PQA on th esaid breker and it registered nothing prir to tripping.The breaker is a magnetis trip.Can the fast switch cause an instantaneous spike in the magnetis flux to trip the breaker?The breaker already ha sthe trip setting to max.
Thanking you all in advance
AMESOLUTIONS