Hi Everybody
Happy Holidays !
Here are my two questions;
Q#1, I am a new start in this area so while specifying the rating of a 120 v panel some thing flashed in my mind.
we have a 3 ph supply of 416/240 v and then a 500 VA 240/120 v transformer is connected to a 15 A breaker on this 416/240 v panel, and this transformer willsupply 7 Compact flourscent lights 20 w each(single phase). Now we can load a breaker up to 80 % but in this case the current is only 2 Amp on breaker side. What will happen when there is a overload may be a single line to ground fault. As there is only phase and neutral on secondary side, so no possibility of line to line fault, but do you think, a 15 Amp breaker having a primary loading of 2 Amp and secondary loading of 4.2 Amp will trip on ground fault. Please advise.
Q #2, We have a power distribution project as normally utilities do the power distribution but the local utility has asked the owners to proceed and it is around 2.5 Sq. km area with around 600 homes. Now, we come under the preview of Electrical Safety authority and that is the hard part, they have come up with so many things which utilites will not even think about doing. Here is my question below:
They have asked us to put a load break switch on every pole from where there is a tap to pad mounted transformer, I was wondering, single pole switching leads to ferroresonance, so should I use a three pole or single pole. If I use three pole then the other two feders will go out of service also, but If I use single pole then there might be ferroresonance.
The other part of this question is The ESA asked for an interlocking mechanism with pad mounted transformer and with all the others which are looped and connected to the one which is having a tap from over head line. What does that mean ?
I hope I have tried to make my self very clear. I would appreciate any word from you gurus.
Best Regards,
Happy Holidays !
Here are my two questions;
Q#1, I am a new start in this area so while specifying the rating of a 120 v panel some thing flashed in my mind.
we have a 3 ph supply of 416/240 v and then a 500 VA 240/120 v transformer is connected to a 15 A breaker on this 416/240 v panel, and this transformer willsupply 7 Compact flourscent lights 20 w each(single phase). Now we can load a breaker up to 80 % but in this case the current is only 2 Amp on breaker side. What will happen when there is a overload may be a single line to ground fault. As there is only phase and neutral on secondary side, so no possibility of line to line fault, but do you think, a 15 Amp breaker having a primary loading of 2 Amp and secondary loading of 4.2 Amp will trip on ground fault. Please advise.
Q #2, We have a power distribution project as normally utilities do the power distribution but the local utility has asked the owners to proceed and it is around 2.5 Sq. km area with around 600 homes. Now, we come under the preview of Electrical Safety authority and that is the hard part, they have come up with so many things which utilites will not even think about doing. Here is my question below:
They have asked us to put a load break switch on every pole from where there is a tap to pad mounted transformer, I was wondering, single pole switching leads to ferroresonance, so should I use a three pole or single pole. If I use three pole then the other two feders will go out of service also, but If I use single pole then there might be ferroresonance.
The other part of this question is The ESA asked for an interlocking mechanism with pad mounted transformer and with all the others which are looped and connected to the one which is having a tap from over head line. What does that mean ?
I hope I have tried to make my self very clear. I would appreciate any word from you gurus.
Best Regards,