MaxMedic
Civil/Environmental
- Feb 3, 2022
- 17
Hello, I am looking into checking to see if what is shown in the section is sufficient for the reliving angle for the rick. The 3/4" anchor bolts are a single bolt spaced at 16" O/C. The brick span/relieving angle span is about 13'-9" and the height of the brick is 15'-0". I believe that I would have to see if the angle can support the weight of the brink then test the connection of the weld. Then check the shear bearing (which I am not sure if its the shear) of the plate which I am proposing to change to a L angle if the plate isn't sufficient. The height) of the 4"x3/8" plate is 2'-3". And lastly I would have to test the 3/4" anchor bolt capacity and breakout from the concrete. I am just not too familiar with calculating breakout when its on the X-plane, I am more familiar with columns and other types of embedment.
Thank you.
Thank you.