I have a brick veneer lintel, in design, that is caught up in a grey area:
My angle needs to span 10'. It supports 40 psf brick veneer. The angle size requested by the architect is a 7" x 4" x 3/8" angle.
The brick above the angle is only 5'-4" tall.
All this being said, I'm trying to determine if the 7 x 4 x 3/8 angle is ok.
If more masonry was above the angle, I could assume triangulation of the veneer (arching action) and the use of tables that I have would be fine, but in this case, I don't think there's enough veneer above the angle, so I think the angle must be designed for the uniform load of the veneer.
As best I can tell, in the BIA Tech Note, it looks like, if the veneer is laterally tied to the building via brick ties (which it is), then the angle can be designed to the allowable stress of 22ksi. If that's the case:
Span = 10'
Veneer Ht = 5'-4"
Load = 213 lb/ft
Moment = 32,000 lb - in
Section Modulus Needed = 32,000/22,000 = 1.45
Section Modulus Provided = 4.42 of a 7" x 4" x 3/8" angle
Deflection = 0.0817 (L/1467)
Bearing Stress = 44 psi
To me, the 7 x 4 x 3/8 looks fine.....but I'm wondering about the allowable stress that BIA recommends, at the 22,000 psi. Seems like it should be less.
Can anybody provide me guidance as to a design guide for angles that have limited veneer above them? There's no other loads.
Thanks guys,
MarinaMan
My angle needs to span 10'. It supports 40 psf brick veneer. The angle size requested by the architect is a 7" x 4" x 3/8" angle.
The brick above the angle is only 5'-4" tall.
All this being said, I'm trying to determine if the 7 x 4 x 3/8 angle is ok.
If more masonry was above the angle, I could assume triangulation of the veneer (arching action) and the use of tables that I have would be fine, but in this case, I don't think there's enough veneer above the angle, so I think the angle must be designed for the uniform load of the veneer.
As best I can tell, in the BIA Tech Note, it looks like, if the veneer is laterally tied to the building via brick ties (which it is), then the angle can be designed to the allowable stress of 22ksi. If that's the case:
Span = 10'
Veneer Ht = 5'-4"
Load = 213 lb/ft
Moment = 32,000 lb - in
Section Modulus Needed = 32,000/22,000 = 1.45
Section Modulus Provided = 4.42 of a 7" x 4" x 3/8" angle
Deflection = 0.0817 (L/1467)
Bearing Stress = 44 psi
To me, the 7 x 4 x 3/8 looks fine.....but I'm wondering about the allowable stress that BIA recommends, at the 22,000 psi. Seems like it should be less.
Can anybody provide me guidance as to a design guide for angles that have limited veneer above them? There's no other loads.
Thanks guys,
MarinaMan