Generator stepup transformer 25kv/345kv Shell Form 650MVA FOA rating. No FOA or FA rating.
We are studying POSSIBLE options to address identified thermal hotspots in the power supply to the fans/pumps. Someone had proposed removal of all cooling power for a brief interval to allow repairs. During this period the transformer would be fully loaded and have no pumps or fans operating.
We are trying to determine what duration if any would it be safe to operate like this.
My concern is that with oil flow greatly reduced (only small amount of natural circulation), we have no ability to determine actual winding temperature. (delta between oil temperature and winding hot-spot will be much higher than it would be with flow).
What do you think? Has anyone ever done it?
=====================================