Background:

-Cast in-situ viaduct, spans ~42m
-3 webs
-6 anchorage in a web
-31 strands in an anchorage
(all fixed at one end, ~12mm dia. each)
-Day 1, stress to 50% design stress for all anchorages

-Day 2, 5 strands in an anchorage were broken while stressing

Any suggestions to this issue?
What the redundancy in strands design(ie 20% or 40%) usually?
What are the measures to rectify the situation?
 
Replies continue below

Recommended for you

If only one strand and it has pulled out of the anchorage wedges you might be OK. But 5 strands broken and it's not even known why they broke, I cannot see anyone accepting the tendon as a whole.

I guess you have to de-stress and replace the tendon.

Zambo



 
11822,

I had a similar disaster to start the year'04. Our fabricator wished me happy new year with the news about a pressure vessel item, designed by me, he was fabricating. At 50% load, during testing, a bolt just snapped into two.

Reason was found later. The guys did not torque this bolt with torque-wrench to specified value, but used their Horse Sense and Hammer. It was over overstressed and taking the load in undue proportion.

Always see that post-tension is applied uniformly and equally. Use Instrumentation, if necessary.
 