GTstartup
Electrical
- Mar 5, 2005
- 422
I have a gap in my knowledge about the interaction of brushless exciters and generator field. I have tried to find some text on line and elsewhere to show me the theory about how field current is generated when an exciter is brushless.
Now I know that the AVR field current is applied to the exciter stator and, due to the rotation of the exciter rotor, transformer action results in an AC current being induced on the exciter field. This in turn is rectifed by rotating diodes and sent to the generator rotor.
But.
The actual exciter current AND voltage is much lower than the generator field current and voltage so this extra power comes from the prime mover.
Can somebody explain the physics of how this is happening?
Primarily,
How does increasing the exciter current by say 10% result in a generator field current increase of 10%? Lets say the exciter current is 20A and the field current 1500A. If I increase the exciter current the field current must increase also. This implies a change in load angle of the generator.
Why does such a small increase in exciter current result in an increase of shaft power? What is the interaction between the increase of exciter current and field current?
Hope you generator gurus can help.
Now I know that the AVR field current is applied to the exciter stator and, due to the rotation of the exciter rotor, transformer action results in an AC current being induced on the exciter field. This in turn is rectifed by rotating diodes and sent to the generator rotor.
But.
The actual exciter current AND voltage is much lower than the generator field current and voltage so this extra power comes from the prime mover.
Can somebody explain the physics of how this is happening?
Primarily,
How does increasing the exciter current by say 10% result in a generator field current increase of 10%? Lets say the exciter current is 20A and the field current 1500A. If I increase the exciter current the field current must increase also. This implies a change in load angle of the generator.
Why does such a small increase in exciter current result in an increase of shaft power? What is the interaction between the increase of exciter current and field current?
Hope you generator gurus can help.