Where do I find some good information (with a picture preferably) on
1. Building VLLR drift limits
2. Diaphragm deflection limits between the MFRS.
I have design guide 3, but that all seems greek. What do they mean drift perp to wall? Which wall, the shearwall or the wall which is perp to this wall. I know you always hear h/400 for the VLLR, but why. Where is that written in stone, and why can a prefab building drift so much more.
Thanks for any help.
Depends on what you are designing for. There are seismic drift limits in the IBC code. Design guide 3 is for serviceability and yes it is very hard to read. Pre-Engineered metal buildings are allowed a limit of L/120 regardless of cladding, which I think is a political thing...lobbyists and all for the metal building association. If you have masonry veneer, then you should use somewhere between L/600 and L/480. A masonry association recommends L/730, but that gets a little crazy. I would use design guide 3 except I would use the masonry veneer limit above. Another thing you can consider is you wind speed. It is based on a 50yr occurrence. Who cares if your brick cracks a little in 50 yrs. You can adjust your serviceability design wind speed by converting it to a 10 yr wind speed and reduce your wind speed by around 30%. The conversion chart is in the back of ASCE 7. Makes a pretty big difference if you can't meet your serviceability drift limit. You still want to set your strength limit using the standard wind speed.