CanuckEngineer
Electrical
- Feb 9, 2009
- 45
Hello All,
I have some questions regarding Emergency Generator distribution systems and how they relate specifically to Canadian/Ontario ESA/CSA codes since this particular installation has been built in Ontario.
First the overview: What we have is a Main-Tie-Main 600V-2500A distribution switchboard. This SWBD provides power for the entire site. This SWBD also acts as the emergency generator paralleling SWBD, there are embedded paralleling generator breakers within the SWBD. The main SOP is that after a utility power failure, the Main breakers open, the qty:3 diesel generators come up to speed and voltage, they parallel and close to the dead bus. The Tie breaker closes.
1. My first question, is that the Main breakers have manual operator push buttons located on them. Currently there is no electrical interlocks wired to these buttons to prevent the Main breakers from being accidentally closed to an unsynched generator bus. The contractor has placed padlocks on them currently to prevent this from happening. However I do not think it is sufficient. Is there any applicable code in CSA 22.2 that states there has to be some form of electrical protection on this breaker?
2. My second questions, we have a three generator system installed, however the engineer has only designed the system with a failure of one generator system via a load shedding system. Basically if one generator fails, loads are dropped and the other two generators take up the remaining load of the building. The engineer however has not designed for a two generator failure situation. Basically right now we have if a two generators fail, the one remaining generator will be overloaded and drop off. My questions is that is there some specific code reference which dictates that load shedding must be implemented all the way down to a one generator running system?
3. My third questions is: The engineer has placed the fire pump breaker upstream of the main breaker, which I understand is per code. The problem is that during a utility fail situation there is a Fire Pump ATS which transfers between the Utility feed to a single generator feed only for the fire pump. Basically if that one generator fails, let's call it G1, then the fire pump is lost however there are still two other running generators in the building. My questions is there any specific code references which dictate that if there is a multiple generator set installation that there has to be some form of redundancy for the Fire Pump distribution?
Much thanks.
I have some questions regarding Emergency Generator distribution systems and how they relate specifically to Canadian/Ontario ESA/CSA codes since this particular installation has been built in Ontario.
First the overview: What we have is a Main-Tie-Main 600V-2500A distribution switchboard. This SWBD provides power for the entire site. This SWBD also acts as the emergency generator paralleling SWBD, there are embedded paralleling generator breakers within the SWBD. The main SOP is that after a utility power failure, the Main breakers open, the qty:3 diesel generators come up to speed and voltage, they parallel and close to the dead bus. The Tie breaker closes.
1. My first question, is that the Main breakers have manual operator push buttons located on them. Currently there is no electrical interlocks wired to these buttons to prevent the Main breakers from being accidentally closed to an unsynched generator bus. The contractor has placed padlocks on them currently to prevent this from happening. However I do not think it is sufficient. Is there any applicable code in CSA 22.2 that states there has to be some form of electrical protection on this breaker?
2. My second questions, we have a three generator system installed, however the engineer has only designed the system with a failure of one generator system via a load shedding system. Basically if one generator fails, loads are dropped and the other two generators take up the remaining load of the building. The engineer however has not designed for a two generator failure situation. Basically right now we have if a two generators fail, the one remaining generator will be overloaded and drop off. My questions is that is there some specific code reference which dictates that load shedding must be implemented all the way down to a one generator running system?
3. My third questions is: The engineer has placed the fire pump breaker upstream of the main breaker, which I understand is per code. The problem is that during a utility fail situation there is a Fire Pump ATS which transfers between the Utility feed to a single generator feed only for the fire pump. Basically if that one generator fails, let's call it G1, then the fire pump is lost however there are still two other running generators in the building. My questions is there any specific code references which dictate that if there is a multiple generator set installation that there has to be some form of redundancy for the Fire Pump distribution?
Much thanks.