On a multistory wood framed project the architect is looking to use UL U925 with AAC block to achieve the fire rating. This detailing does not have a gap between the wood framed walls and the AAC block.
Per ASCE 7-10 section 12.12.3 "All portions of the structure shall be designed and constructed to act as an integral unit in resisting seismic forces unless separated structurally by a distance sufficient to avoid damaging contact as set forth in this section."
Since we do not extend the floor diaphragm across the firewall we are creating 2 buildings on the same property adjacent to one another. The requirements above appear to directly contradict each other.
Based on the anticipated shearwall deflections we would want to account for 4" of differential movement between the 2 buildings (ASCE 7-10 equation 12.12-2).
How are other engineers detailing this condition?
Per ASCE 7-10 section 12.12.3 "All portions of the structure shall be designed and constructed to act as an integral unit in resisting seismic forces unless separated structurally by a distance sufficient to avoid damaging contact as set forth in this section."
Since we do not extend the floor diaphragm across the firewall we are creating 2 buildings on the same property adjacent to one another. The requirements above appear to directly contradict each other.
Based on the anticipated shearwall deflections we would want to account for 4" of differential movement between the 2 buildings (ASCE 7-10 equation 12.12-2).
How are other engineers detailing this condition?