I am designing a built-up "cruciform" column as part of a rigid frame (using R=3.0) to resist wind and seimic loads. I am uncertain of how to design the weld of the WT webs to the web of the continuous wide flange column. I am thicking about doing a shear flow calculation for the bending forces in the column and sizing a fillet weld on either side to the WT webs. Is there any other forces I need to add in?
I noticed that the seismic design manual (section 2.3.2b) calls for a zone extending 12" above and 12" below the beam where the WT's are attached with a CJP weld AND a pair of reinforcing fillet welds. Is this recommendation a good idea (or just extra expense), if we are in a low seismic area and not using a special or intermediate moment frame? I appreciate any comments.
I am designing a built-up "cruciform" column as part of a rigid frame (using R=3.0) to resist wind and seimic loads. I am uncertain of how to design the weld of the WT webs to the web of the continuous wide flange column. I am thicking about doing a shear flow calculation for the bending forces in the column and sizing a fillet weld on either side to the WT webs. Is there any other forces I need to add in?
I noticed that the seismic design manual (section 2.3.2b) calls for a zone extending 12" above and 12" below the beam where the WT's are attached with a CJP weld AND a pair of reinforcing fillet welds. Is this recommendation a good idea (or just extra expense), if we are in a low seismic area and not using a special or intermediate moment frame? I appreciate any comments.