cmsurfsup
Mechanical
- Apr 29, 2013
- 4
I'm trying to verify the burst disk capacity of an existing system. The over pressure scenario is a pump continuing to pressurize a tubing system with a valve closed downstream. I'm using the resistance flow method because the tubing between the pump and the burst disk is 1/4" but the burst disk holder is 1/2", so the coefficient of discharge method doesn't apply. I was trying to follow the Fike burst disk sizing examples for the resistance to flow method but it really doesn't correlate to a pump pressure source. So how do I verify the burst disk capacity?
The particulars:
Pump flow = 0.0145 cfm
tubing internal diameter = .083"
burst disk size = 1/2" NPT
Krgl = 5.39
The pressure loss between the pump and the burst disk consists of a tube section, tee branch, expansion.
The burst disk outlet vents to atmosphere.