Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Burst heating coil 1

Status
Not open for further replies.

coolmedown

Mechanical
Jan 19, 2005
4
0
0
US
I have a heating coil 138/115 Deg C flow & return temperatures, design conditions. It is only 2 weeks old and recently burst at a support strap connecting the the flow and return header.
Before the incident under low load condition the return temperature was going back at 40 deg C. Is this normal and ok?. The control valve was only approximatly 10% open during this time maintaining off coil conditions smothly.
The coil supplier doesnt think the water should be going back so low and has blamed this on the controls system.

I am trying to figure out the thermodynamics of the coil re LMTD etc...and figure out why the coil burst.
Please help!!
 
Replies continue below

Recommended for you

ChasBean1 said something about the water that was bothering me too. How can you have water at 138C? If it is that hot shouldn't it be steam?

I wonder if the coil supplier looked at the installation site before he sold the coil? The pin hole failure sure sounds like a weld defect to me. Which wouldn't be caused by stress, thermal or mechanical.

Is this a replacement coil, or is it a brand new installation?



 
Icanfix, you can have HW at that temperature given enough pressure. This has to be a high pressure system. But if your control valve is barely cracked and you have cold outside entering temperature, you could easily flash to steam at the control valve and then condense and subcool in the coil. You could even develop a situation where all the heating takes place in the first 1/4 coil, and have such a low flow and low temperature in the last 3/4 of the coil that your AVERAGE air outlet temperature is normal but you freeze water in lower parts of the coil...
 
Hmmm. Several things about this discussion bother me.

The quoted hot water temperatures are high. Yep, one can achieve these easily enough in a pressurized system. I've worked with such in the past. But where is THIS system installed, and why are they using a pressurized system? Pressurized systems, of adequate pressure to allow heating water temps as described, are expensive and generally only used when situation dictates it's use.

Next, coil manufacturer's claim that coil only tested and suitable for the ONE given supply and return temp, and may fail under any other condition is at best bogus and silly. How in the world do you do a startup and shut down if that's the case? Did they ship it to the site in a sealed and enviormentally controlled container to maintain temps within specs? That's ridiculous. Normal such a rating as they are arguing would be the conditions under which they can guarantee a specific performance of heat transfer. And is otherwise meaningless. It certainly can not reasonably mean that the coil will physically fail under any other circumstances whatsoever.

What are the coil manufacturer's instructions concerning warm up, cool down rates and times? In high performance, high energy systems, where thermal shock is a concern and issue, it is normal for equipment maker to provide specific operating info, stating something like "Do not allow equipment to warm up (or cool down)faster than 20 degrees per minute." Something to that effect. One sees these types of instructions commonly in high energy systems which damage due to overfast heating or cooling of system is expected to cause damage or shorten expected and design operational lifetime of equipment. Did coil manufacturer provide such instructions, if not, then they don't have much of a leg to stand on in their claims that the too low return temp damaged their coil. If they truly designed coil to such close (and flimsy) tolerances, they should've been clear about this. Actually, they should get into another line of business.

Now, that return temp you got is a problem. Shouldn't have caused the failure. One would expect that upon startup or shut down one might well see such a difference between supply and return. But that return temp shouldn't be "normal". That is, shouldn't occur normally during operation of properly designed and controlled equipment. I tend to agree with another poster that coil might be oversized. But, really, you haven't given much info for us to really know.

In my experience, which isn't all that great IMHO, there are questions here. Normally I'd expect that a coil that needs to have a specific supply and return water temp within some faily close tolerances, would achieve this by varying GPM, with control one control point looking at HW supply temp, keeping it steady. And another, the one for the coil, watching return temp and modulating to maintain that, as versus watching air temp. Another control of some sort, bypass damper or whatever, taking care of maintaining air temp parameters.

This is an interesting discussion. But raises a lot of questions in my mind.

In any event, pin hole leak as you describe sounds more like a manufacturing defect to me that anything else. ie Welder or brazer got a bit carried away with heat attaching strap, dug too deep into material of pipe. Thermal expansion and contraction, not unexpected ... quite normal, as one would get this in start up and shut down conditions even if everything else was working right, broke free strap and pulled away too thin spot on pipe.

Just my opinion.

In any event, that big of a deltaT shouldn't be during normal operations. Coil likely too big. Or maybe control valve on inlet, and inlet on top of coil? I've seen that screwup before.


 
Hi folks

I've just picked up this thread and it seems like youv'e exhausted almost all avenues. However have you considered external forces. Is the coil piped up in such a way that it is not affected by external forces due to expansion.

If the pipework connecting on to the coil is subject to a large amount of expansion, there will be a lot of movement and stress generated which might affect the coil and cause it to burst??

Just a thought.



Friar Tuck of Sherwood
 
Have a metalurgical lab analyse the coil at the break. Pressure temperature rating of copper fittings show that at lower temperature they are capable of higher pressure so the 40°C should not be a problem
 
Status
Not open for further replies.
Back
Top