rajendrarohra1978

Electrical
Jul 16, 2013
19
0
0
SA
Hi, We had Bus Bar Differential operated during Transformer Energisation ( 75MVA)
THe CT's are measruning input & output currents for Bus Differential
Has someone observed similiar issue. The Bus is healthy & also teh Transformer.

Thanks in advance

 
Replies continue below

Recommended for you

I remember years ago studying the theory and operation of an electro-mechanical transformer differential protection relay.
First there was a CT ratio to compare the primary current with the secondary current.
This function was then biased to balance out errors caused by no ,oad losses.
Another feature balanced out load dependant losses.
I don't remember how inrush was accommodated, possibly with a time delay.
The point is, there is a lot going on when a transformer is energized.
If this was infrequent or a one time thing, the transformer energization current may have saturated a CT.



--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Issues I’ve seen for misoperating differentials:
- loose/bad CT wire connection
- miswired
- transformer compensation not set right in microprocessor relay
- CT shorting terminal left in
-2nd ground in CT circuit
-test switch left open
There are certainly more but these have happened to me or my coworkers.
 