rajendrarohra1978
Electrical
- Jul 16, 2013
- 19
Hi all,
We have 34.5 KV switchgear with Bus Bar protection relay 7UT6 ( Siemens Siprotec)
The system has incomer & around 4 outgoing feeders. The system is working fine till recently when the new feeder for different plant was connected. The feeder was energized & minimum load was available. owever when the major load was started the Bus bar Protection for Bus-A section operated. The previous commissioning report during installation of 34.5 KV system showse testing report for all CT's & their polarities. We suspect the polarity of CT in new feeder may not be OK. Is there no Harmonic inrush blocking feature same as Transformer differential not available in Bus bar differential.
Thanks.
We have 34.5 KV switchgear with Bus Bar protection relay 7UT6 ( Siemens Siprotec)
The system has incomer & around 4 outgoing feeders. The system is working fine till recently when the new feeder for different plant was connected. The feeder was energized & minimum load was available. owever when the major load was started the Bus bar Protection for Bus-A section operated. The previous commissioning report during installation of 34.5 KV system showse testing report for all CT's & their polarities. We suspect the polarity of CT in new feeder may not be OK. Is there no Harmonic inrush blocking feature same as Transformer differential not available in Bus bar differential.