c p for aboveground storage tank

Status
Not open for further replies.

Mohamedhassanmido

Materials
Sep 3, 2013
24
How I calculate no of sacrificial anodes and their position per any tank by equations?
 
Replies continue below

Recommended for you

Hi,

The following parameters are required in order to determine the current requirement:

- Type of coating of the storage tank bottom
- Operating temperature of the tank
- Surface area of the tank
- A factor included in the surface area accounting for the surface area of the welds between the tank bottom plates
- The type of anode you wish to use (assuming magnesium if it is a sacrificial anode system)
- The basic current density assumed, commonly considered as 22mA/m2

The basic idea is to multiply the surface area by the coating breakdown factor by the adjusted current density based on the operating temperature. Once you arrive at a current requirement, you can estimate the mass of anodes required based on the type of anode (consumption rate) and design life amongst other parameters.

I tried to provide you with the basics. However, you need to get your hand on a reliable cathodic protection handbook. There is more to it.

Best of luck.
 