I have performed measurements on a 50 kV, 3x1x1200 mm2 AL PEX cable with 96 mm2 CU screen.
The cable system has a length at 6700 m. At the midpoint the screens are earthed to reduce screen voltage the system has earthed screen at both ends. Cables are laid in flat formation.
A VLF test has been made indicating no abnormalities.
The AC resistance is specified as 0,24 Ohms/phase.
We measure a value of 0,75 Ohms/ phase that is 3 times specified value !
The DC-resistance is measured to 0,4 Ohms corresponding to specified value.
What might be the reason that we measure 3 times AC resistance compared with cable supplier spec.
Best regards
HH