Hi Guys,
I have following query regarding NEC code requirements for cable ampacity derating.
We have following situation for calculation of motor cable sizes for cables leaving from one of the MCC in Substation.
Cable Laying Condition: Uncovered Cable Tray
Nos. of Power Cables in tray: Cables for 9 Nos. 150HP, 3Ph, 460V Motor
Cables are kept touching to each other.
Conductor Type: Copper
Conductor Insulation: XHHW (90 deg. C)
MCC Terminal temperature: 75 deg. C
Ambient Air temperature 40 deg. C
Motor FLA for 3Ph, 460V, 150HP motor = 180A as per Table 430.250, Motor Cable to be sized for = 1.25 * 180 = 225A each.
Thus, cable size selected to carry the current = 4/0 AWG Copper Conductor, which is suitable for carrying 230Amp load current, which satisfies 75 deg.C MCC terminal in line with NEC 110.14(C).
Temperature Correction Factor = 0.91 --- for ambient temperature variation as per NEC Table Table 310.15(B)(1)(1).
NEC 392.22(A)(1)(a) requires that multiconductor cables with 4/0AWG or larger to be laid in single layer, however, does not specify any mandatory spacing between the cables.
Considering the huge quantum of cables leaving electrical substation, it is not possible for us to maintain the spacing of one diameter and it is required to install cables touching to each other.
NEC clause 392.80(A)(1)(c) says “Where multiconductor cables are installed in a single layer in uncovered trays, with a maintained spacing of not less than one cable diameter between cables, the ampacity shall not exceed the ambient temperature-corrected ampacities of multiconductor cables , with not more than three insulated conductors rated o through 2000 volts in free air, in accordance with 310.14(B)”
Accordingly, above clause is applicable only in case of maintained spacing of not less than one diameter.
Also, NEC 310.15(C)(1) does not apply, as there are not more than 3 current carrying conductors in a multiconductor cable.
Thus, it is not clear to me about how to adjust ampacity of cables, in case of multiconductor cables installed touching to each other.
Any advice on above will be highly appreciated.
Thanks in advance,
SK
I have following query regarding NEC code requirements for cable ampacity derating.
We have following situation for calculation of motor cable sizes for cables leaving from one of the MCC in Substation.
Cable Laying Condition: Uncovered Cable Tray
Nos. of Power Cables in tray: Cables for 9 Nos. 150HP, 3Ph, 460V Motor
Cables are kept touching to each other.
Conductor Type: Copper
Conductor Insulation: XHHW (90 deg. C)
MCC Terminal temperature: 75 deg. C
Ambient Air temperature 40 deg. C
Motor FLA for 3Ph, 460V, 150HP motor = 180A as per Table 430.250, Motor Cable to be sized for = 1.25 * 180 = 225A each.
Thus, cable size selected to carry the current = 4/0 AWG Copper Conductor, which is suitable for carrying 230Amp load current, which satisfies 75 deg.C MCC terminal in line with NEC 110.14(C).
Temperature Correction Factor = 0.91 --- for ambient temperature variation as per NEC Table Table 310.15(B)(1)(1).
NEC 392.22(A)(1)(a) requires that multiconductor cables with 4/0AWG or larger to be laid in single layer, however, does not specify any mandatory spacing between the cables.
Considering the huge quantum of cables leaving electrical substation, it is not possible for us to maintain the spacing of one diameter and it is required to install cables touching to each other.
NEC clause 392.80(A)(1)(c) says “Where multiconductor cables are installed in a single layer in uncovered trays, with a maintained spacing of not less than one cable diameter between cables, the ampacity shall not exceed the ambient temperature-corrected ampacities of multiconductor cables , with not more than three insulated conductors rated o through 2000 volts in free air, in accordance with 310.14(B)”
Accordingly, above clause is applicable only in case of maintained spacing of not less than one diameter.
Also, NEC 310.15(C)(1) does not apply, as there are not more than 3 current carrying conductors in a multiconductor cable.
Thus, it is not clear to me about how to adjust ampacity of cables, in case of multiconductor cables installed touching to each other.
Any advice on above will be highly appreciated.
Thanks in advance,
SK