Hello,
I am calculating a cable (selecting fuse/protection, calculating voltage drop) for star/delta starter of squirrel-cage motor by IEC standard, IEC 60364-4-43.
When there are two cables in parallel that supply some load, let's say two cables that supply some electrical cabinet from a substation, we take maximum allowed current as two times maximum allowed current of one cable, and take cross section in voltage drop calculation as two times cross section of one cable. Assumption is that load is divided equally between cables, of course cables are of the same type and same length.
In case of star/delta starter currents are not halved in the branches of circuit, they are square root of 3 times smaller than current that passes through protection device. Now, is it correct to do calculation for this case by looking at it like having "1.73 cables in parallel"? I think this will give correct result when sizing cable and proving it is protected from overcurrents.
I am calculating a cable (selecting fuse/protection, calculating voltage drop) for star/delta starter of squirrel-cage motor by IEC standard, IEC 60364-4-43.
When there are two cables in parallel that supply some load, let's say two cables that supply some electrical cabinet from a substation, we take maximum allowed current as two times maximum allowed current of one cable, and take cross section in voltage drop calculation as two times cross section of one cable. Assumption is that load is divided equally between cables, of course cables are of the same type and same length.
In case of star/delta starter currents are not halved in the branches of circuit, they are square root of 3 times smaller than current that passes through protection device. Now, is it correct to do calculation for this case by looking at it like having "1.73 cables in parallel"? I think this will give correct result when sizing cable and proving it is protected from overcurrents.