Cable current rating

aslamajec123

Electrical
Aug 24, 2009
6
we have been calculating ampacity of subsea 400kV 3 core 2500 sq.mm and 2000 sq.mm Cu cables using CYMCAP software . But we noticed that there is only marginal increase (Les than 10A) in the current carrying capacity of 2500 sq.mm cable over 2000sq.mm. Where as there has been significant increase in ampacity when we checked for single core cables of same cross section and also with 3 core cables with smaller cross sections . Can you tell me what would be the main reasons for no significant increase in the ampacity of 3 core 2500 sq.mm cable over 2000 sq.mm ? Is this well expected ?
 
Replies continue below

Recommended for you

Skin effect comes to mind.
Some of the things affecting ampacity;
The temperature limit of the insulation and or surroundings.
The ability to radiate the heat losses so as to limit the temperature rise.
Consider;
The three conductor cable has less effective surface area per conductor to radiate heat.
At 400 kV, the insulation will be quite thick and form a thermal insulation as well as an electrical insulation.
There will be a temperature drop through the insulation and the internal temperature will be considerably higher than the surface temperature.
The 2000 sq mm cable will be equivalent to almost two inches diameter of solid conductor. Stranding will increase this diameter.
The skin effect will be considerable.
Parallel cables or hollow conductors are often used at this current level. (IPS Bus, That is, aluminum tubing constructed to Iron Pipe Sizes is often used as a conductor at high current levels due to skin effect.)
From 2000 sq.mm.to 2500 sq. mm. you are increasing the cross sectional area by 25% but you are increasing the surface area to radiate heat by only 12%.

Just for fun, try running your calculations with a 1 inch hollow core and with 1 1/2 inch and 2 inch hollow cores.
The results may lead you to investigate the feasibility of having cables constructed around a core of rope or some other substance.

Bottom line, a 10 Amp increase does seem low.
In addition to the other factors, I suspect that the thermal insulation may be the biggest issue.
Again, just for fun, try running the calculations with several steps of thinner insulation and see if the results suggest a reason.
 
Current carrying capacity is not directly proportional to the cross section due to the heat transfer characteristics. If you look at the tables in the National Electrical Code (and other codes, I assume), this is clearly evident. At some point it is more economical to run multiple smaller conductors in parallel.
 
Do have the cut sheet for the cable you are considering? The southwire catalog shows an 8.7% increase going from 4000 kcmil to 5000 kcmil conductors

It is pretty common for EHV cables to be much larger than medium voltage cables. Going with smaller cables also nearly doubles the charging current.
 