A contractor ran cable in conduit on a project. The outer sheath had so many tears in it after the cable pull that we were concerned that the underlying layer of insulation was also damaged - it appears they did not use pulling compound. The company offered to Meg test which they did successfully. We later learned that cable passes the meg test even with blatantly exposed copper showing from the insulation and we do know there was at least one case where they did damage the insulation and had exposed copper. Ought we accept the meg test result and accept
the cable or should we fight to have the cable replaced? It will certainly become litigatious if we refuse to accept.