Cable Failure in straight joint
sajuthomas
3
In my project, there was cable failure for 22kV cable straight joint in normal operating time. These cable were installed in covered trench.
Anybody can share What would be the reason for cable failure?
In the absence of external influence such as disturbance by heavy equipment or such, failure is usually traceable to an incorrectly installed splice.
old field guy
Such premature failures are mainly due to either bad workmanship or incorrect application of the cable termination materials or in some cases due to both factors.
to be more stringent in the selection of licensed cable jointers and must follow jointing kit's instruction strictly.
some afterlaying tests are useful too, especially PD Diagnostics which is a very sensitive to incorrect workmanship
Poor application of product. PD may or may not reveal poor workmanship; however, other dielectric testing such as tan delta evolution may have revealed any treeing or paths to ground throught the dieletic prior to energization. The preperation of the cable for the installation of the splice is critical.
In my experience, I second these opinions. Workmanship, followed by miss-application, followed by manufacturing defect.