We had an interesting situation come up here recently...wondering if anyone had seen anything like this:
The city was seeing intermittent trips on a 15kV breaker which was tied to an underground feeder. Within a week, one of the phases (they run each phase in a separate conduit), faulted. They pulled the faulted cable out and replaced it. Within a week, another phase faulted. Both of the faults occurred at a 90 degree turn in the conduit. The conduits were installed as pvc with steel elbows at the turns. The cable manufacturer said that by using the steel elbows, the magnetics would create heat causing the breakdown. The city only was using about 60 percent of that cable's capacity so I can't see how the magnetic heating effect could create enough heat to push the cable's temperature high enough to create that fault. Any thoughts/comments?
The city was seeing intermittent trips on a 15kV breaker which was tied to an underground feeder. Within a week, one of the phases (they run each phase in a separate conduit), faulted. They pulled the faulted cable out and replaced it. Within a week, another phase faulted. Both of the faults occurred at a 90 degree turn in the conduit. The conduits were installed as pvc with steel elbows at the turns. The cable manufacturer said that by using the steel elbows, the magnetics would create heat causing the breakdown. The city only was using about 60 percent of that cable's capacity so I can't see how the magnetic heating effect could create enough heat to push the cable's temperature high enough to create that fault. Any thoughts/comments?