Hi Guys,
I am in Australia where we use IEC standards and we don't have any requirements for UL listing of protective devices.
We have a class 30 overload application with a soft starter with line contractor. What sort of branch protection should I be using?
The distributor is telling me that we should use a magnetic only (you guys call it an MCP) breaker upstream and let the soft starter do overload protection for the feeder cable, motor cable, and contactor.
What do you think? Will the thermal protection in the soft starter protect the feeder cable and motor cable, even if the soft starter is set up for a class 30 overload?
What about the contactor? can the soft starter be relied upon to do thermal overload protection for it too?
Cheers