Cable Protection - Protecting Shield Wire from a Ground Fault? 1

Status
Not open for further replies.

BINGMD

Electrical
Jul 26, 2005
37
Protection Guru,

When checking 34.5kV feeder relay ground element settings for cable protection, is it necessary to consider protecting a cable from a feeder ground fault with all the ground fault current returned via the shield wire (1/3 netural)?

Thank you,
Best Regards,
Bing
 
Replies continue below

Recommended for you

You need to be concerned about the short-time thermal rating of the shield. Even with a separate external ground wire, the shield will carry a lot of current during ground faults. It's generally not a big problem. Okonite has data on this in their cable handbook, IIRC.
 