Hi Everybody,
I was working on pulling 600 MCM teck90 armoured cable from basement of a building to 10 th floor through electrical rooms on each floor. The current is 2000 Amp, that means 3 cables/ phase. As I wantd some specs, I spoke to NEXANS and ALCAN.
The ALCAN gus told me that you should go for a Alcan cable and that also three conductor cable, as this will lead to less voltage drop and you can run three cables each three conductor side by side as one has to be very care ful of the phase imbalance which arises due to different lengths of cable. Here is arrangement below:
All phase in one section: Three conductor cable:
O 0 O O
OO OO OO OO
Then I spoke to NEXANS guy, ofcourse both were application engineers not sales guys, he told me as I have three conductors per phase then I should go for single conductor cable and each in a traingular configuration to have less voltage and then he said if you have even no of conductors per phase then you should go for a rectilinear configuration. All factors are attributed due to voltage drop. A B C phase in one section adn neutral in middle.
N N N
O O O
O O O O O O O O O
Now when I explained this story to my big boss, he said we will go in a different way, and that will be like below but in outward direction horizontally.
A B C N
O O O O
O O O O
O O O O
so this is All phase in parallel outward way.
Now here is my question, which arrangement is good and why?
Please advise any free software available where I can test this configuration.
Why cable pulling is an issue and as an engineer how to figure out that I should not leave it to contractor and come out my self with the exact bending configurations.
I appreciate you time always.
Regards,
I was working on pulling 600 MCM teck90 armoured cable from basement of a building to 10 th floor through electrical rooms on each floor. The current is 2000 Amp, that means 3 cables/ phase. As I wantd some specs, I spoke to NEXANS and ALCAN.
The ALCAN gus told me that you should go for a Alcan cable and that also three conductor cable, as this will lead to less voltage drop and you can run three cables each three conductor side by side as one has to be very care ful of the phase imbalance which arises due to different lengths of cable. Here is arrangement below:
All phase in one section: Three conductor cable:
O 0 O O
OO OO OO OO
Then I spoke to NEXANS guy, ofcourse both were application engineers not sales guys, he told me as I have three conductors per phase then I should go for single conductor cable and each in a traingular configuration to have less voltage and then he said if you have even no of conductors per phase then you should go for a rectilinear configuration. All factors are attributed due to voltage drop. A B C phase in one section adn neutral in middle.
N N N
O O O
O O O O O O O O O
Now when I explained this story to my big boss, he said we will go in a different way, and that will be like below but in outward direction horizontally.
A B C N
O O O O
O O O O
O O O O
so this is All phase in parallel outward way.
Now here is my question, which arrangement is good and why?
Please advise any free software available where I can test this configuration.
Why cable pulling is an issue and as an engineer how to figure out that I should not leave it to contractor and come out my self with the exact bending configurations.
I appreciate you time always.