tc7
Mechanical
- Mar 17, 2003
- 387
We are setting up a temporary winch system which will utilize a generator to drive several 480V-3phase motors.
I have determined that the connecting cable size should be size 1 or 1/0 based on start-up currents of ~134 amps (I'm told this start-up current will last for 7-8 seconds and normal load current will settle to ~20 amps).
Our contractor insists on using size 4 wire (stranded,Class THWN), stating that the Free Air ampacity of size 4 wire is 125 amps and within the working limits of this application.
So I see in NEC Table 310-17 it would seem this contractor may be correct if we do not install the cable inside conduit, but rather just laying cable on the ground and unprotected. Will I be violating any other Code requirement for temporary installations?
Advice/thoughts on any of the above gladly rec'd.
Thanks,
Tom
I have determined that the connecting cable size should be size 1 or 1/0 based on start-up currents of ~134 amps (I'm told this start-up current will last for 7-8 seconds and normal load current will settle to ~20 amps).
Our contractor insists on using size 4 wire (stranded,Class THWN), stating that the Free Air ampacity of size 4 wire is 125 amps and within the working limits of this application.
So I see in NEC Table 310-17 it would seem this contractor may be correct if we do not install the cable inside conduit, but rather just laying cable on the ground and unprotected. Will I be violating any other Code requirement for temporary installations?
Advice/thoughts on any of the above gladly rec'd.
Thanks,
Tom