SSKLC
Electrical
- Jan 15, 2024
- 10
Hi,
I am trying to size cables from Star Delta Starter to Motor
During Star connection,
Load Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/3 (33%) of actual FLC
Load Current in Cable from SWGR – Motor Term. U2, V2, W2 = 1/3 (33%) of actual FLC
Starting Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/3 (33%) of actual Starting Current
Starting Current in Cable from SWGR – Motor Term. U2, V2, W2 = 1/3 (33%) of actual Starting Current
During Delta Connection,
Load Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/√3 (58%) of FLC
Load Current in Cable from SWGR – Motor Term. U2, V2, W2 = = 1/√3 (58%) of FLC
(Note that reclosing current transient during star to delta transition is ignored as present only for very small duration)
For Star Connection,
Running VD = √3 x (33% of FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
Starting VD = √3 x (33% X starting current Mulitplier x FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
For Delta Connection,
Running VD = √3 x (58% of FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
Based on above, worst case cable size to be selected for cables between Star Delta Starter to Motor.
Please advise if I am missing anything.
I am trying to size cables from Star Delta Starter to Motor
During Star connection,
Load Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/3 (33%) of actual FLC
Load Current in Cable from SWGR – Motor Term. U2, V2, W2 = 1/3 (33%) of actual FLC
Starting Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/3 (33%) of actual Starting Current
Starting Current in Cable from SWGR – Motor Term. U2, V2, W2 = 1/3 (33%) of actual Starting Current
During Delta Connection,
Load Current in Cable from SWGR – Motor Term. U1, V1, W1 = 1/√3 (58%) of FLC
Load Current in Cable from SWGR – Motor Term. U2, V2, W2 = = 1/√3 (58%) of FLC
(Note that reclosing current transient during star to delta transition is ignored as present only for very small duration)
For Star Connection,
Running VD = √3 x (33% of FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
Starting VD = √3 x (33% X starting current Mulitplier x FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
For Delta Connection,
Running VD = √3 x (58% of FLC) x (2xL) x (RcosØ + XsinØ) / (No.of runs X V)
Based on above, worst case cable size to be selected for cables between Star Delta Starter to Motor.
Please advise if I am missing anything.