rockman7892
- Apr 7, 2008
- 1,178
I am currently reviewing a project in which the cables between the generator Exciter Compartment (AVR) and the generator field compartment are being replaced. I was curious if there were any guidelines or references for verifying or confirming the required ampacity of these cables?
Generator is a 230kVA Gas Turbine unit with its Field Amps listed as 1,870A @ 375V DC. The exciter itself has a listed continuous ampacity of 2150A @ 420V DC and a Ceiling of 3400A @ 576 VDC.
Does this exciter cable typically have its ampacity sized to meet the rated field amps based on the generator nameplate, or is it sized based on the capability of the exciter itself? I would think its based on the rated machine field amps but wanted to make sure I wasn't missing something.
If determining the ampacity based off the rated field amps is it typical to use the field amps at generator full load (1,870A) or do you typically put some margin on this value such as 105%, 110%, etc...? Generator datasheet does not provide specific overload values (105%, etc...) but does provide saturation curves with Field Amps vs Armature Voltage/Current. There are multiple curves on this plot with two of the curves showing the field amps above the rated field amps for conditions labeled as "Saturation at rated armature amps-rated PF" and "Saturation at rated arm amps - 0 PF". Doe these saturation considerations need to be taken into account when determining required ampacity of cable?
Thanks for the help!