This should be a quick one:
For Medium Voltage applications, lets say I have a 2.6MW generator and I need to size the cable for this.
I normally go 2.6MW / 0.8PF to give me 3.25MVA (worst case PF, they typically run at 1PF).
And then go 3.25MVA / root3 / 4.16kV = 451A.
And then on top of that I add the 125% factor to give me 563A for minimum cable ampacity.
My colleagues say, that since you are already including a safety buffer in the 0.8PF, you don't need to add the 125% additional safety factor anymore....
I disagree, b/c the PF during operation can range anywhere between 0.8 to 1.0. So you can't rely on that for cable ampacity calcs.....
Thoughts?
For Medium Voltage applications, lets say I have a 2.6MW generator and I need to size the cable for this.
I normally go 2.6MW / 0.8PF to give me 3.25MVA (worst case PF, they typically run at 1PF).
And then go 3.25MVA / root3 / 4.16kV = 451A.
And then on top of that I add the 125% factor to give me 563A for minimum cable ampacity.
My colleagues say, that since you are already including a safety buffer in the 0.8PF, you don't need to add the 125% additional safety factor anymore....
I disagree, b/c the PF during operation can range anywhere between 0.8 to 1.0. So you can't rely on that for cable ampacity calcs.....
Thoughts?