sonic02

Electrical
Feb 13, 2011
22
Hi there,

Can you run 1kV,teck 90 3C#1 AWG power cable, a 4/0 AWG grounding conductor and Instrumentation Cables (in a 4" rigid PVC conduit) in the same trench as mechanical hot and cold water pipes?

Sonic
 
Replies continue below

Recommended for you

You may get away with a cold water line depending on the AHJ, but field experience is that when the insulation degrades on the hot water pipe, the cables will be subjected to a higher than designed ambient temperature.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
With hot water pipes your cables will be derated. Also they may damage the insulation over the time and you may have to replace the cable completely.
 