Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

CABLE VS. CONDUIT TO CONNECT MOTOR

Status
Not open for further replies.

polareng

Electrical
Nov 24, 2006
16
0
0
US
I need to connect a 10HP, 3ph motor to contoller box. Do I have to use conduit or can I use cable? The run is less than 10ft. Am I bound by NEC 400.7 Uses Permitted? because it is not specifically Not Permitted per 400.8. I just find it hard to believe that this would not be allowed.
 
Replies continue below

Recommended for you

Agreed!

I would just say that transitioning from conduit to cable can be a bit of a pain because you have to provide a junction box to make the extra connections verses transitioning to liquid-tite and just pulling the wires straight through to the motor/etc.

Keith Cress
Flamin Systems, Inc.-
 
UL listed shielded motor lead cable for drive-motor leads is available from Pirelli, Okonite, and recently, Belden.

I believe that each is listed for open (non-conduit) installation under controlled conditions.
 
Status
Not open for further replies.
Back
Top