CodyK
Mechanical
- Jun 9, 2020
- 18
If the calculated CFMs of a load calculation don't match stock equipment, is it best to match the required tonnage and let the cfm's be lower? Is it justifiable to purchase a larger fan?
I recently did a manual J calculation using CoolCalc and the cooling BTUH = 35,000 but the room by room cfm add up to 1900. My guess is just to get a 3 ton unit and use the nominal 1200 cfm that come with most equipment. I mostly do commercial equipment replacement calculations and HAP usually results in cfm/ton well above stock equipment. Typically we just size the equipment based on the tonnage in the load calcs and the cfm per room is lower than calculated. Is this the correct approach?
I recently did a manual J calculation using CoolCalc and the cooling BTUH = 35,000 but the room by room cfm add up to 1900. My guess is just to get a 3 ton unit and use the nominal 1200 cfm that come with most equipment. I mostly do commercial equipment replacement calculations and HAP usually results in cfm/ton well above stock equipment. Typically we just size the equipment based on the tonnage in the load calcs and the cfm per room is lower than calculated. Is this the correct approach?