I have a question that is posing a problem regarding calculating the mains input power being consumed by a 3 phase induction motor that has the following parameters:
20HP
400Vac 50Hz
PF 0.9
Efficiency 0.85
I was led to believe that is was simply 20HP x 746W = 14.92kW but I think this is wrong?
Should you first calculate the motors line current i.e.
IL = Power (kW) / VL x 1.73 x PF x n
14,920 /400 x 1.73 x 0.9 x 0.85 = 28.18A
then
Pin = VL x IL x 1.73 x PF (does efficiency need to be used as well?)
Pin = 400 x 28.18 x 1.73 x 0.9 = 17.56kW
I have searched everywhere but I cannot seem to find correct solution to this the simple problem.
Could someone advise on how to do this correctly?
Also when you find the input power, is it this the power consumed by each phase or the TOTAL power consumed by the machine?
Many Thanks in advance,
Regards
Martin