edwardmp2009
Chemical
- Dec 15, 2011
- 16
At our company, we currently have a 3-cell counter current flow induced draught cooling tower used for cooling service water for vacuum pumps. Literature states that vacuum pumps operate at maximum capacity when service water temperature is 15 degrees Celsius and below. The design data available for the service cooling tower is shown below:
Number of cells = 3
Capacity = 87 cubic meters / h of water in each cell (total = 261 cubic meters / h)
Type = induced draught cooling tower
Dimensions of each cell:Length = 1 m; width = 1 m; height = 1.5 m
Current cooling water temperature in summer = 35 degrees Celsius
Cooling tower return water temperature = 47 degrees Celsius
Maximum ambient air temperature = 42 degrees Celsius
Inlet air wet bulb temperature = 24.5 degrees Celsius
From the above data, it can be seen that the temperature approach is 10.5 degrees Celsius and the cooling range is 12 degrees Celsius.
The following air data is not available at this stage:
1. air flow rate
2. dry bulb temperature of outlet air
3. wet bulb temperature of outlet air
We wish to modify the cooling tower by adding a 4th cell of similar dimensions. How can we calculate the cooling range or temperature approach for the new design, that is the cooling water temperature under the new design modification?
Number of cells = 3
Capacity = 87 cubic meters / h of water in each cell (total = 261 cubic meters / h)
Type = induced draught cooling tower
Dimensions of each cell:Length = 1 m; width = 1 m; height = 1.5 m
Current cooling water temperature in summer = 35 degrees Celsius
Cooling tower return water temperature = 47 degrees Celsius
Maximum ambient air temperature = 42 degrees Celsius
Inlet air wet bulb temperature = 24.5 degrees Celsius
From the above data, it can be seen that the temperature approach is 10.5 degrees Celsius and the cooling range is 12 degrees Celsius.
The following air data is not available at this stage:
1. air flow rate
2. dry bulb temperature of outlet air
3. wet bulb temperature of outlet air
We wish to modify the cooling tower by adding a 4th cell of similar dimensions. How can we calculate the cooling range or temperature approach for the new design, that is the cooling water temperature under the new design modification?