jordi29
Mechanical
- Jan 5, 2009
- 7
Hello all,
First time poster here.
I have a CW AHU (55Tons Nominal) and I am trying to figure out how many actual tons of cooling I am currently getting out of it. For this, I need to know the gpm's going through the coil. Since I don't have a flow meter, I believe there is a way to calculate gpm, if I can read a pressure drop (diff) from a specific location on the unit's CWS and CWR lines.
Can anyone offer any assiatance on this? I am basically trying to figure out if the unit is starving for air or starving for water. Here are the current conditions on the unit:
- CWS Temp: 42'F
- CWR Temp: 56'F
- Supply Air Temp: 55.5'F
- Return Air Temp: 70.5'F
- CW Valve Open: 100%
- Supply Air Setpoint: 55'F (this is min value allowed)
Thanks in advance!
jordi29.
First time poster here.
I have a CW AHU (55Tons Nominal) and I am trying to figure out how many actual tons of cooling I am currently getting out of it. For this, I need to know the gpm's going through the coil. Since I don't have a flow meter, I believe there is a way to calculate gpm, if I can read a pressure drop (diff) from a specific location on the unit's CWS and CWR lines.