CoolCat83
Mechanical
- Aug 29, 2022
- 5
Recently started a new job as an assistant project manager bit of a career change so no real experience in construction. Owner/lead engineer is putting an 8 unit addition onto one of his houses, and typically hires out to get designs stamped by engs who specialize in whatever, but is having me review things just so I can get up to speed and hopefully stamp off when I feel I'm competent enough. The structure is built, and now just being finished. He asked me to calculate the heat load, and don't have anything beyond the web / an HVAC course I did through school 15 years ago.
Dimensions of building are 28 x 74 x 35 high, with a lip that extends 38' x 28 x 9' high over the existing building. (So a forth story on current 38 x 28 building, plus building/extending those 4 stores 74' back)
so 7000 sq ft of wall space (8" ICF) R = 24
only 100 sq ft of windows R = 4
3200 sq ft ceiling, R 30, 5" spray foam
105 sq ft of doors, R 10
2100 sq ft floor space, foam insulated concrete R 30
Assume 70 deg F difference ( 0 to 70) during peak heating load yields:
21k BTU/hr through walls
2k BTU/hr through windows
8k BTU/hr through ceiling
1k BTU/hr through doors
5k BTU/hr through floor
So not even 40k BTU/hr which seems extremely low. Add in another 50k BTU/hr or so to heat incoming air based around .5 changes per hour, so not even 100k. - But still seems low. More so when you consider that a good deal of the heat will be recovered via HRVs. I've read a good deal about how efficient ICF can be, but the owner who's built other places based on rules of thumb figured he would need 2 heating units, one 200k BTU/hr, and a 100k BTU/hr as a compliment/backup. Is there something obviously wrong? It seems like a fairly straight forward calculation and additionally I've been reading about how common it is for heating units to be criminally oversized, since it's a culmination of "better safe than sorry", people who don't know how to do the calcs themselves, and the financial incentives to sell bigger units.
I also filled out the ASHRAE excel work sheet, and that took into account several other factors such as inefficiencies in the heating system, and 0 HRV recovery, but even still it came in around only 120k BTU/HR. Am I missing something obvious here?
Dimensions of building are 28 x 74 x 35 high, with a lip that extends 38' x 28 x 9' high over the existing building. (So a forth story on current 38 x 28 building, plus building/extending those 4 stores 74' back)
so 7000 sq ft of wall space (8" ICF) R = 24
only 100 sq ft of windows R = 4
3200 sq ft ceiling, R 30, 5" spray foam
105 sq ft of doors, R 10
2100 sq ft floor space, foam insulated concrete R 30
Assume 70 deg F difference ( 0 to 70) during peak heating load yields:
21k BTU/hr through walls
2k BTU/hr through windows
8k BTU/hr through ceiling
1k BTU/hr through doors
5k BTU/hr through floor
So not even 40k BTU/hr which seems extremely low. Add in another 50k BTU/hr or so to heat incoming air based around .5 changes per hour, so not even 100k. - But still seems low. More so when you consider that a good deal of the heat will be recovered via HRVs. I've read a good deal about how efficient ICF can be, but the owner who's built other places based on rules of thumb figured he would need 2 heating units, one 200k BTU/hr, and a 100k BTU/hr as a compliment/backup. Is there something obviously wrong? It seems like a fairly straight forward calculation and additionally I've been reading about how common it is for heating units to be criminally oversized, since it's a culmination of "better safe than sorry", people who don't know how to do the calcs themselves, and the financial incentives to sell bigger units.
I also filled out the ASHRAE excel work sheet, and that took into account several other factors such as inefficiencies in the heating system, and 0 HRV recovery, but even still it came in around only 120k BTU/HR. Am I missing something obvious here?