DavidButler
Mechanical
- Aug 18, 2015
- 25
Attached is a diagram showing how thermal energy storage (TES) can be installed in parallel between chiller and load. The 2nd page is an excerpt from an ASHRAE Journal article by Kent Peterson on which this design is based. When only the chiller is operating, the zone valve on the fan coil is closed and the chiller will charge the tank. When only the fan coil is operating, the chiller zone valve is closed and the fan coil will discharge the tank. When both are operating, the tank will either charge or discharge depending on which flow rate is greater.
In the diagram, I show the fan coil having the larger flow rate, so the tank will discharge the difference between the two flow rates. This is an elegant solution as it avoids the need for a dedicated pump for TES with associated valves and controls.
When only one pump is operating, the loop pressure drop includes the Tee-branch into and out of the tank, but what I don't understand is how to estimate the PD at the Tee that each pump "sees" when both are operating. Hopefully someone here can assist. Thx
.