Calculating Moment Capacity
JSF-Office
3
This might sound basic, but I’m new to bridge design and am currently working on verifying the capacity of a 3' by 6' deck cover using LBFoster’s proprietary 4 1/4" interlock with concrete overfill product. The attached brochure provides the section modulus for the composite section, but I would like to understand how to calculate the moment capacity based on the provided information.
Here’s my understanding so far:
For steel, the moment capacity is calculated as:
M=S×Fy
For a composite section, I believe the moment capacity is calculated as:
S effective=S steel + n × Sconcrete
Where n is the ratio of the modulus of elasticity of steel to concrete: n=29000 ksi / 4500 ksi=6.4n
Using 6" spacing per the provided table, I calculate Seffective S as:
S effective=4.88+(6.4×63.82)= 415.9in3
To apply the moment capacity equation, I’m assuming Fy=36 ksi so:
M=415.9 in3×36 ksi=14,971.7 k-in
Is this approach correct? is there other checks that AASHTO requires in using such systems, Any feedback or suggestions are appreciated!
Thank you.
S for a composite section is more accurately calculated as the summation of Io + Ad^2 for the component sections, in the same way as you'd calculate the section modulus for other built-up shapes, except for transforming the concrete to an equivalent area of steel by dividing the width of the section by "n".
That makes perfect sense. Thank you, BridgeSmith.