Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Calculating Moment Capacity

Status
Not open for further replies.

JSF-Office

Structural
Joined
Apr 16, 2020
Messages
3
Location
US
Hello,

This might sound basic, but I’m new to bridge design and am currently working on verifying the capacity of a 3' by 6' deck cover using LBFoster’s proprietary 4 1/4" interlock with concrete overfill product. The attached brochure provides the section modulus for the composite section, but I would like to understand how to calculate the moment capacity based on the provided information.

Here’s my understanding so far:

For steel, the moment capacity is calculated as:

M=S×Fy

For a composite section, I believe the moment capacity is calculated as:

S effective=S steel + n × Sconcrete

Where n is the ratio of the modulus of elasticity of steel to concrete: n=29000 ksi / 4500 ksi=6.4n

Using 6" spacing per the provided table, I calculate Seffective S as:

S effective=4.88+(6.4×63.82)= 415.9in3

To apply the moment capacity equation, I’m assuming Fy=36 ksi so:

M=415.9 in3×36 ksi=14,971.7 k-in

Is this approach correct? is there other checks that AASHTO requires in using such systems, Any feedback or suggestions are appreciated!

Thank you.

post.jpg
 
S for a composite section is more accurately calculated as the summation of Io + Ad^2 for the component sections, in the same way as you'd calculate the section modulus for other built-up shapes, except for transforming the concrete to an equivalent area of steel by dividing the width of the section by "n".
 
That makes perfect sense. Thank you, BridgeSmith.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top