Calculating Resistance and Reactance from positive sequence fault current 1
asela115
5
Dear All,
I know following two parameters
a) Maximum three phase fault current in amperes (A) and phase angle in degrees (B).
I want to calculate the positive sequence resistance (R) and reactance (X) from above two variables for a symmetric system. I couldn't figure out a way to find R and X values using just these two parameters. However I noted somebody has calculated this using following formula for same purpose (unfortunately couldn’t verify who did this in my workplace).
R = A * COS (PI()*B/180) X = A * SIN (PI()*B/180) where A is the three phase fault current and B is the phase angle
If someone can guide me to figure out the correct formula and the relation above, please
A word picture;
Construct a right triangle with hypotenuse = A (Amperes)
and
Angle = B
Hypotenuse = current = 1/Z = (1/Impedance)
Base = Real Current component = 1/R = (1/Resistance)
Altitude = Reactive Current component = 1/X = (1/Reactance)
You should be able to solve this with reciprocals, sines and cosines.
Is this the formula when the angle is reported in radians?
Bill
"Why not the best?"
Jimmy Carter
Type this into google:
symmetrical components filetype:xlsx
There are a few good excel calculators out there that are very simple.
Hi Waross,
thanks for the explanation
is it like , 1/Z = (current / voltage)
(do i need to have voltage as well?)
In my opinion, if you intend to calculate the impedance in ohm-not in p.u.-then you’ll need the voltage.
A=V/(R+Xi)=V(R-Xi)/(R^2+X^2) then:
Iactiv=V*R/(R^2+X^2) Ireact=-V*X/(R^2+X^2) TAN(B)=Ireact/Iact=-X/R
A=SQRT(Iactiv^2+ Ireact^2)
A=V*SQRT(R^2+X^2)/(R^2+X^2)=V/SQRT(R^2+X^2)
X=TAN(B)*R
Then:
A=V/R/SQRT(1+TAN(B)^2) and from here:
R=V/(A*SQRT(1+TAN(B)^2)
(1+TAN(B)^2)=1+SIN^2(B)/COS^2(B)=1/COS^2(B)
R=V/A*COS(B) X=V/A*SIN(B)
B has to be radians then if B it is done in degrees then B[rad]=pi()/180*B[degrees].
I agree with 7anoter4 as long as you use phase-neutral voltage for V.
Thank you, jghrist and sorry for the delay.
You are right. Since this is a symmetric 3 phases system [direct sequence system] the rated voltage has to be phase-to-phase voltage. Then the involved voltage here has to be V/sqrt(3).
Hi !!
I will explain in a reverse way , by taking an example . Just ignore the material which is not relevant to you .
Suppose you have to calculate the 3 phase short circuit at point A as shown below .
As shown in blue is how we calculated the short circuit current , but in your case you already know the SC current , thus
Z = Un/(1.732*Isc).
Once you have Z , then you can calculate , R/Z=Cos(theta)
As you said you already have theta.
I hope this will help.