SteelPE
Structural
- Mar 9, 2006
- 2,759
I asked this question a long time ago (maybe 8 -10 year ago). At the time I didn’t get much response.
In regards to calculating seismic loads in accordance with ASCE (specifically 7-10). ASCE 7-10 requires you to include 20% of the seismic loads for flat roof snow loads greater than 30psf.
In many jurisdictions I work in, the code will provide a Pg and a minimum Pf. Often Pf is greater than what you would calculate using Pg. For example, a structure with Ce=Ct=Is=1.0 with a code required Pg=40psf would yield a Pf= 28 psf snow load (in accordance with ASCE 7). However, the local code requires a minimum Pf = 35 psf for this area.
So, the question is, how would you handle this with regards to calculating seismic loads. Would you use the 28 psf (therefore no additional seismic load) or 35 pf (7psf additional load)? From what I can tell, the local code gives no guidance as to what should be used.
I can see an argument both ways.
In regards to calculating seismic loads in accordance with ASCE (specifically 7-10). ASCE 7-10 requires you to include 20% of the seismic loads for flat roof snow loads greater than 30psf.
In many jurisdictions I work in, the code will provide a Pg and a minimum Pf. Often Pf is greater than what you would calculate using Pg. For example, a structure with Ce=Ct=Is=1.0 with a code required Pg=40psf would yield a Pf= 28 psf snow load (in accordance with ASCE 7). However, the local code requires a minimum Pf = 35 psf for this area.
So, the question is, how would you handle this with regards to calculating seismic loads. Would you use the 28 psf (therefore no additional seismic load) or 35 pf (7psf additional load)? From what I can tell, the local code gives no guidance as to what should be used.
I can see an argument both ways.