I wanted to calculate what kind of cost was associated with starting some of our larger motors here in the plant. The best way to do this was to first equate a kWH rating for the motor starting and then work this number into my electrical rates.
To get a kWH rating for the motor starting, I calculate a kilo-watt second kWS value for the motor starting and then convert this to a kWH value. The following is an example I did.
2300hp motor at 4.16kV
FLA=312A
LRA= Dont have exact value but will estimate at 8x FLA =2496A
Acceleration time (Acc_time) = 10s
kWS used during start = (V)(LRC)(Acc_time)(1.73)
Note: I perform this calculation example ignoring PF for
the time being and assume all current is real.
Therefore kWS = (4.16)(2496)(10)(1.73) = 179632 kWs
Convert kWs to kWH = (179632kWs/1)(1m/60s)(1h/60m)=49.89kWH
We do not get charged a PF penalty however we do have a kW demand charge. Averaging out the kWH rate and kW demand charge we get charged about .075cents/kWH.
Therefore: 49.89kWH * .075 c/kWH = $3.75
Does $3.75 sound right for starting this large motor or am I missing something here?
The only thing I am not factoring in, is how this start effects the demand charge for the rest of the monthly kwH however ignoring this for a second and looking strictly at cost of motor starting is this calculation method correct?