How can I calculate the output power from a 3 phase UPS with unbalanced loads?
Load Voltage(Vrms)R-Y 409.8 Y-B 414.3 B-R 414.1
Load Voltage R-N 237.4 Y-N 238 B-N 239.7
Load Current(Arms) R 79 Y 27.7 B 41.3 N 68.4
Our engineer attached a Fluke scope meter to each phase voltage and current and then added them together. This came out at approximately 60kVA. But if you use P=V*I*1.73 for each phase and then sum these results this adds up to 105.6kVA.
Anyone help?

UPS engineer
 
Replies continue below

Recommended for you

P=V*I*1.73 is for a "balanced" 3 phase power system, that is when I is equal in all three lines and V= V line to line.

For unbalanced system, calculate per phase values and add them up.

For each phase power, the formula is V*I where V is line to neutral or (Vll/1.732).

Rafiq Bulsara
 
Notice that if you take your 105 kVA and divide by 1.73 you get the engineer's solution. That's a hint that you mis-applied an equation somewhere.
 
Probably used the line voltage and not the phase-neutral voltage...?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Our engineer attached a Fluke scope meter to each phase voltage and current and then added them together. This came out at approximately 60kVA.

How was that connected and measured? Given your numbers, the only way I can get close to 60 kVA is by using the peak instead of RMS L-N voltages.

SUM( Vln * Il ) = 41.7 kVA

Vln = line-neutral voltages (Vr-n, etc.)
Il = line currents

Using the line to line voltages, the proper formula is

SUM( Vll * Il )/ 1.73 = 72.3/ 1.73 = 41.6 kVA

Vll = line to line voltage

which is close enough.

But if you use P=V*I*1.73 for each phase and then sum these results

But you don't. That will work for a balanced situation where V is Vll and V and I are the balanced line to line voltage, line current. But then you don't sum them.
 
Note:
kW is power.
KVA is apparent power.
You are calculating apparent power, not true power. {rant off}
Yes, I get 35.2 KVA

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Blondel's theorem - in a system of N electrical conductors, N-1 electrical meter or wattmeter elements, when properly connected, will measure the electrical power or energy taken.

Your system is a 4-wire, so 3-element metering is adequate.

So, 35.2 kVA is the correct answer!
 