Thermo01
Mechanical
- Nov 21, 2019
- 12
Hi there,
I'm looking for some help on calculating the duty of a chilled water computer room air handler
I've taken some readings (from calibrated equipment)on both the water and the air side and calculated the duty from these figures but the figures are no where near the same.
Air on 29'C
Air off 17'C
Density 1.2Kg/m3
Airflow 6m3/s
Using Q = M x Cp x DT this gives me a duty of 6 x 1.2 x 12 = 86.4Kw
However taking figures on the water side from the same unit at the same time I get the following figures
Water inlet 12'C
Water Outlet 7'C
Specific heat capacity 4.19Kj/Kg
Flow rate 2.483L/s
Using Q = M x Cp x DT this gives me a duty of 2.48 x 4.19 x 5 = 51.956
Can anyone advise on to where I'm going wrong.
Thanks
I'm looking for some help on calculating the duty of a chilled water computer room air handler
I've taken some readings (from calibrated equipment)on both the water and the air side and calculated the duty from these figures but the figures are no where near the same.
Air on 29'C
Air off 17'C
Density 1.2Kg/m3
Airflow 6m3/s
Using Q = M x Cp x DT this gives me a duty of 6 x 1.2 x 12 = 86.4Kw
However taking figures on the water side from the same unit at the same time I get the following figures
Water inlet 12'C
Water Outlet 7'C
Specific heat capacity 4.19Kj/Kg
Flow rate 2.483L/s
Using Q = M x Cp x DT this gives me a duty of 2.48 x 4.19 x 5 = 51.956
Can anyone advise on to where I'm going wrong.
Thanks