Dear friends
If anybody know how to calculate the transformer power consumption in KW,
please let me know
with best wishes
P. Manohar rao
 
Replies continue below

Recommended for you

Is this question correct?, I do not think of a transformer as a power consumer (apart from losses, which may be the originators question??)it has a power rating at which it will effectivly operate.
Watts or kilowatts is dirived from volts x amps or as the other responder said kva multiplied by the power factor.

am I correct ??
 
Power consumption = no-load losses plus load losses.

no-load (iron) losses at rated voltage and load (copper) losses at rated load can be found from factory test reports. To get no-load losses at other than rated voltage multiply by (V/Vrated)². For load losses at a different load, multiply by (kVA/kVArated)².
 
As a rule of thumb, if you're looking say to design an HVAC system to cool the transformer, 2% of transformer kVA rating will give you a reasonable heat load in kW.
 