We have tried to shorten the construction time of a 6 storey hospital building. There are 1626 supply, return and exhaust boxes controlled by a Honeywell ComfortPoint system. In the majority of areas, there are 1 or 2 ceiling diffusers for each VAV box. During construction, we blanked off duct work to lower floors and started calibrating VAV boxes on upper levels as spaces had duct work and diffusers installed and became clean. So in essence the calibration was completed in 6 stages over 2 months. To complicate matters, when all duct and construction was finally complete, basement air flow was found to be marginal and not at design. In some areas, the boxes starve for air.
In addition, we are now discovering that the flow values for our boxes will drift over time and the sensed flow is different from the measured flow. The controllers require a new calibration factor. The new factor isn't radically different but it is enough for the supply and exhaust volumes to noticeably change over time. This change alters the building pressures. Doors don't close, airflow whistles through the building, etc. In some cases, volumetric offsets are changed from design to accommodate correct air flow movement.
The TAB technicians did visually verify VAV controller operation, pressure tube orientation, etc. But the calibration program did not allow any other commissioning of the VAV boxes. As far as I am aware, end-to-end checks from graphics to VAV box has not been completed.
There are no quadrant dampers at duct trunks to each floor. Should these be installed to allow for the TAB agent to proportionally balance the air to each floor?
Did the sequential method of applying flow reference values as each floor was complete add to our final error?
What is the correct sequence(s) for calibrating multiple levels of VAV boxes?
While I am in favour of maintaining first principles, is there a quick way to re-calibrate the building?
Thank you
In addition, we are now discovering that the flow values for our boxes will drift over time and the sensed flow is different from the measured flow. The controllers require a new calibration factor. The new factor isn't radically different but it is enough for the supply and exhaust volumes to noticeably change over time. This change alters the building pressures. Doors don't close, airflow whistles through the building, etc. In some cases, volumetric offsets are changed from design to accommodate correct air flow movement.
The TAB technicians did visually verify VAV controller operation, pressure tube orientation, etc. But the calibration program did not allow any other commissioning of the VAV boxes. As far as I am aware, end-to-end checks from graphics to VAV box has not been completed.
There are no quadrant dampers at duct trunks to each floor. Should these be installed to allow for the TAB agent to proportionally balance the air to each floor?
Did the sequential method of applying flow reference values as each floor was complete add to our final error?
What is the correct sequence(s) for calibrating multiple levels of VAV boxes?
While I am in favour of maintaining first principles, is there a quick way to re-calibrate the building?
Thank you