I like to have valves with more than 1 setpoint from different controllers.
FOR EXAMPLE, we have a flow control taking gas from a point going to a compressor. Put if 1 out of 4 compresors goes down, the pressure will rise and overload the engine, so we use a low select relay that sends the output from a pressure controller to the valve. As the pressure is rising, the pressure controller sends a lower signal to shut the valve, the relay selects the lowest signal which is pressure control. The flow controller wants more gas, and sends a higher signal to try to open the valve.
So a high or low select can can have multiple set points. On liquid meters we have a 3 way system, Inlet to the meter pressure that can not be too low, outlet from the meter run, that won't let the outlet presure get to high, and flow control set point. all threen varibles met, one control valve.